Recommended Posts

Any electricians on here? I'm looking for someone to help me with a small project. I have called a few local companies without success.

I need more outlets in the garage, and I want to run a new circuit for it. The current breaker box has one open slot, and even though I don't expect to need more circuits I think a sub-panel is in order.

I'm looking for someone to install the sub-panel and connect to the existing box for me. Once that is done I will handle the rest of the cable runs/outlets. I'm sure I could do the install but with the potential risks I feel better with someone who does this for a living.

This seems like a fairly simple job if someone is in the Columbia area willing to take on a side project. 

Link to comment

What amp service is the "Main" panel? If the Main is 200 amp you will have room. If the main is just 100 amp you will need to upgrade your service. You can not tie into the Main panel above the main disconnect.

With a 200 amp service you can run a feed to the sub panel with out issue.

Link to comment
1 hour ago, analog_kidd said:

It's easier than you think to wire that up. The hard part will be snaking the wire and making it look nice. 

I have worked with electric a bit, and this does seem simple. Kill the power, connect the feed....my wife disagrees so I'm willing to pay someone who knows what they are doing.

As far as looks, I am doing surface mount conduit anyways, so I was thinking a surface mount panel would be fine as well. Mount it next to the existing panel, one hole in the drywall to snake the cable through...

Edited by jonathon1289
Link to comment
51 minutes ago, RED333 said:

What amp service is the "Main" panel? If the Main is 200 amp you will have room. If the main is just 100 amp you will need to upgrade your service. You can not tie into the Main panel above the main disconnect.

With a 200 amp service you can run a feed to the sub panel with out issue.

The main is 200 amp. I thought about just filling in the last breaker slot for this new circuit, but figured the small cost is worth it to do a sub-panel in case future expansion is needed.

Link to comment

Just where are you planing on hooking up the wire in the main panel? From what you are describing it does not sound like you have enough room for a double pole 100 amp breaker.

Link to comment
34 minutes ago, RED333 said:

Just where are you planing on hooking up the wire in the main panel? From what you are describing it does not sound like you have enough room for a double pole 100 amp breaker.

Move one of the existing breakers over to the new panel?

I have a local company coming out Tuesday to look and give me an estimate (hopefully they show up this time)....will see what they say, worst case I just install a 20amp breaker to completely fill the existing panel, and only worry about future expansion if it is ever needed.

Link to comment
  • 2 weeks later...

I was finally able to get 2 electricians out here this week to look at what I wanted. They suggested going with a tandem 20amp breaker instead of attempting the sub-panel install and moving circuits over due to cost....since I don't expect any future electrical expansion I agreed.

Install was completed to a junction box below my service panel, using 12/3 romex. He wired it as both black/red hot, with a shared neutral, briefly explaining that it is allowed per code as a multiwire branch circuit since the breaker / both circuits are on the same leg/phase. It wasn't really what I had envisioned, but didn't get time to discuss with the tech due to schedule conflicts. From talking to someone else and reading online it should be fine though, or I can unhook it and run a 2nd piece of romex to make it two isolated 12/2 runs (dedicated hot/neutrals).

Now to get conduit run where I need it....

Thanks for the info and suggestions in here.

 

ETA: Read some more, calling to discuss the install tomorrow, but I will get this fixed to 2 completely isolated circuits as I had originally intended. I don't want the shared neutral overload risk. And garage wiring requires GFCI protection, which isn't as straightforward with a shared neutral. So getting this wired as I intended is the best solution, wish had been here for all of the install to get it done right to start with.

Edited by jonathon1289
Link to comment

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now

TRADING POST NOTICE

Before engaging in any transaction of goods or services on TGO, all parties involved must know and follow the local, state and Federal laws regarding those transactions.

TGO makes no claims, guarantees or assurances regarding any such transactions.

THE FINE PRINT

Tennessee Gun Owners (TNGunOwners.com) is the premier Community and Discussion Forum for gun owners, firearm enthusiasts, sportsmen and Second Amendment proponents in the state of Tennessee and surrounding region.

TNGunOwners.com (TGO) is a presentation of Enthusiast Productions. The TGO state flag logo and the TGO tri-hole "icon" logo are trademarks of Tennessee Gun Owners. The TGO logos and all content presented on this site may not be reproduced in any form without express written permission. The opinions expressed on TGO are those of their authors and do not necessarily reflect those of the site's owners or staff.

TNGunOwners.com (TGO) is not a lobbying organization and has no affiliation with any lobbying organizations.  Beware of scammers using the Tennessee Gun Owners name, purporting to be Pro-2A lobbying organizations!

×
×
  • Create New...

Important Information

By using this site, you agree to the following.
Terms of Use | Privacy Policy | Guidelines
 
We have placed cookies on your device to help make this website better. You can adjust your cookie settings, otherwise we'll assume you're okay to continue.