We just recently lost power to an entire circuit of outlets (seven outlets, no lights) in our five year old house. I found the last one in the chain and disconnected them one by one tracing the circuit back via an external wire and the continuity setting on my DMM - there are six standard outlets with a GFCI outlet being the first (as far back as I can trace it, that is) in the circuit. After the GFCI I have no idea where the circuit may go, I assume back to the breaker panel as every other outlet, light, etc is accounted for on other circuits.

Unfortunately, the GFCI is at the front door entry way, so it is surrounded on three sides by brick and the the fourth side abuts the front door, so getting to the wiring behind the box to trace it is nearly impossible. At this point, I think there's an open in the wiring between the breaker (which is new and tests fine) and the GFCI outlet (which is also new). What do you, as electricians, do to find an open to repair such an event? Is there some sort of tracing rig that will work on a non-energized (open) circuit to help trace the wire in the wall?

Any help appreciated, thanks in advance...

Link to comment
  • Replies 21
  • Created
  • Last Reply

Top Posters In This Topic

Top Posters In This Topic

A broken wire is real unlikely. About the only problems I've ever seen with wire has been electricians that created shorts because of sloppy cable prep. The GFCI outlets in my house are wired to protect everything on the circuit, so if the circuit goes down, it's always a GFCI trip.

If it is a broken wire somewhere, you can do your continuity checks with a long extension cord. Kill power on the circuit, plug the cord into the outlet in question, and drag the other end to where you want to make your check.

Link to comment

Replaced both the GFCI and the breaker to be sure, no go. Did just find that the disposal and dishwasher are on the same circuit and are working fine. Now I have to try to pull the outlet from underneath the sink to see if something has come loose...

Link to comment
Hrmm, very strange - when the breaker is turned off, I'm still getting a 40vac reading on the line on my DMM (when it's on, I get the full 120vac).

That's a little scary. Are you sure it's 40 volts? You could easily pick up 40 millivolts of stray on an auto ranging meter.

Link to comment

The neutral (white) is always connected to the neutral buss in the panel. The hot (black) runs thru the breaker. The ground (bare), is connected to the ground buss in the panel. The neutral and ground busses are connected together in the panel. In most cases, they're the same buss (shared).

Link to comment

Is there some sort of tracing rig that will work on a non-energized (open) circuit to help trace the wire in the wall?

I'm no electrician, but there is a product that generates a tone, readable by a second instrument. Sold in a package with both "sender" and "receiver." Should be able to trace the tone from wherever you place the tone generator all the way back to the box. Seems that Home Depot or Lowes used to carry one or two brands of these. Sorry, but I can't remember the name. I've used one a couple times to trace telephone and security wiring when I was helping a bud do some work. It was old (or at least looked old), so I can't vouch that they are still available.

Edit: Both parts required batteries for power, so they worked with no line voltage.

Link to comment
Guest bkelm18
I'm no electrician, but there is a product that generates a tone, readable by a second instrument. Sold in a package with both "sender" and "receiver." Should be able to trace the tone from wherever you place the tone generator all the way back to the box. Seems that Home Depot or Lowes used to carry one or two brands of these. Sorry, but I can't remember the name. I've used one a couple times to trace telephone and security wiring when I was helping a bud do some work. It was old (or at least looked old), so I can't vouch that they are still available.

Edit: Both parts required batteries for power, so they worked with no line voltage.

Circuit tracers/breaker finders are great little tools. However, I'm not sure how well they work through walls. Well, since the GFI and the breaker aren't the cause, and you say certain things on the circuit are working while others do not, that definitely points to a loose broken connection somewhere. Lines don't "just break". Unless you have rodent issues then I'd be willing to bet that the line is fine. Check around for loose connections, including the neutrals in the breaker box. Corrosion can also lead to these types of things though I rarely see that indoors. Another nifty little tool is an outlet tester. They cost less than $5 at the home improvement stores. It's little thing you plug into the outlet and it's got three lights. Depending on which lights light up, it tells you if the circuit is wired correctly and if not, what wires are at fault. Of course this only works if you've got line voltage at the outlet. Best of luck.

Link to comment
Circuit tracers/breaker finders are great little tools. However, I'm not sure how well they work through walls. Well, since the GFI and the breaker aren't the cause, and you say certain things on the circuit are working while others do not, that definitely points to a loose broken connection somewhere. Lines don't "just break". Unless you have rodent issues then I'd be willing to bet that the line is fine. Check around for loose connections, including the neutrals in the breaker box. Corrosion can also lead to these types of things though I rarely see that indoors. Another nifty little tool is an outlet tester. They cost less than $5 at the home improvement stores. It's little thing you plug into the outlet and it's got three lights. Depending on which lights light up, it tells you if the circuit is wired correctly and if not, what wires are at fault. Of course this only works if you've got line voltage at the outlet. Best of luck.

Circuit tracers will work thru a wall. I've never seen a rodent chew through a solid #12 wire. They may chew the insulation off and cause a short. My bet is that a wire came loose in an outlet box, either off the back of a plug, or out of a wire nut.

Link to comment
Guest bkelm18
Circuit tracers will work thru a wall. I've never seen a rodent chew through a solid #12 wire. They may chew the insulation off and cause a short. My bet is that a wire came loose in an outlet box, either off the back of a plug, or out of a wire nut.

I have. ;)

Link to comment

First things first. turn off power, remove "line" side from GFCI. cap the neutral and hot and turn on the power. remove nut on hot (black) and check volts to ground. if no power, do the same for the "load" side of the GFCI. The "Line" side should be your hot. a lot of electricians get this wrong and ruin the outlet. it will not reset, if you put in the new GFCI like the first, wrong, then it will not reset properly either.

if neither wire has voltage then you can test continuity by wire nutting the hot and ground on one side (with power off) and checking at the panel to make sure you don't have a break. check again by wire nutting the neutral and ground.

Let me know from here if all is well, my credentials are 6 years of trouble shooting electrical systems in residential and commercial.

Link to comment
Guest bigbovine

remove nut on hot (black) and check volts to ground

Please do not remove that nut, As he says it is hot. You can easily stick the tester into that nut. Wouldnt wanna accidentaly touch that open wire would you?

Link to comment
That's one helluva critter :) Usually, their little heads will start smoking before they get all the way through. I've found lots of electrocuted mice over the years.

Working electric signs, I have found petrified mice before in restaurant neon transformer boxes in ceilings..................Or crispy baby birds in spring time in outside neon stuff. Nothing like trying to pull one of those out of the box and they break in half..............:)

Link to comment

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now

TRADING POST NOTICE

Before engaging in any transaction of goods or services on TGO, all parties involved must know and follow the local, state and Federal laws regarding those transactions.

TGO makes no claims, guarantees or assurances regarding any such transactions.

THE FINE PRINT

Tennessee Gun Owners (TNGunOwners.com) is the premier Community and Discussion Forum for gun owners, firearm enthusiasts, sportsmen and Second Amendment proponents in the state of Tennessee and surrounding region.

TNGunOwners.com (TGO) is a presentation of Enthusiast Productions. The TGO state flag logo and the TGO tri-hole "icon" logo are trademarks of Tennessee Gun Owners. The TGO logos and all content presented on this site may not be reproduced in any form without express written permission. The opinions expressed on TGO are those of their authors and do not necessarily reflect those of the site's owners or staff.

TNGunOwners.com (TGO) is not a lobbying organization and has no affiliation with any lobbying organizations.  Beware of scammers using the Tennessee Gun Owners name, purporting to be Pro-2A lobbying organizations!

×
×
  • Create New...

Important Information

By using this site, you agree to the following.
Terms of Use | Privacy Policy | Guidelines
 
We have placed cookies on your device to help make this website better. You can adjust your cookie settings, otherwise we'll assume you're okay to continue.